back to article IBM smacks rivals with 5.0GHz Power6 beast

The rest of the server world can play with their piddling 2-3GHz chips. IBM, meanwhile, is prepared to deal in the 5GHz realm. The hardware maker has unveiled a Power6-based version of its highest-end Unix server - the Power 595. The box runs on 32 dual-core 5GHz Power6 processors, making it a true performance beast. This big …

COMMENTS

This topic is closed for new posts.

Page:

  1. kain preacher

    VIsta

    How fast will vista bun on this machine ??

  2. Ashlee Vance (Written by Reg staff)

    Re: VIsta

    I'm told that Vista buns in at 47 on the hot cross linpack benchmark and 817 on SPEC_finger

  3. Matt Bryant Silver badge
    Coat

    RE: Vista

    Yes, but who would eclair to run Vista given the choice?

    Taxi!

  4. Alan Donaly
    Coat

    There's no video card

    how can it bun Vista without a Nvidia 8800 GT or butter.

  5. Anonymous Coward
    Thumb Up

    Mainframes...

    They were cool.... huh uh huh huhhuh..

    If I was like so rich I was like lost on what to do with it... Like y'know even the private jet wasn't cool enough...

    http://blog.searchenginewatch.com/blog/060707-063500

    ...I'd get one of those - dude - they rock.

    (VMS come back all is forgiven.)

  6. Lee T.
    Coat

    RE: VIsta

    vista is such a raise-ource hog it would probably cookie the processors.

    COco!

  7. Colonel Zander

    Yeah, but...

    How does this compare to the new Macs from Apple? Shoddy reporting as usual from Mr. Vance, he never looks at how these so called 'enterprise' systems stack up to the best computers on the planet....what is he afraid of? Is he thinking his overlords at Sun, IBM, and HP will crush him like a bug? Or that they will withhold his monthly stipend?

  8. John
    Happy

    Re: VIsta

    Those buns are not so hot, what with all that water cooling gear.

    However they may still be cross.

  9. Anonymous Coward
    Anonymous Coward

    Is it a power beast as well?

    So IBM has to resort to extreme water cooling in order to reduce this thing's power requirements on the data centers they are deployed in.

    A) Does this help make for a more "beastly" price compared to a Sun based soution?

    B) Even if this cooling solution reduces the power draw by 40% percent over previous Power solutions, is it still more power hungry than a Sun solution?

    I'm not a Sun fanboy, just curious. Also very suspicious about what IBM did not reveal as opposed to what they did reveal.

  10. Brett Brennan
    Coat

    But the Vista Experience is only 3...

    due to no drivers being available to use the whopping huge hot cores for VGA video output. So the entire system will still take 2-3 hours to copy a 4.7GB DVD image from one 500 drive array to another...

    Mine's the one with a VIA Eden system in the pocket running off of 8 "C" cell batteries...

  11. Pierre

    I was in love

    Before y'all mentionned Vista.

    I might still get one of these shiny racks. That's on my todo list. Just before "buy a Vista-certified box for personal use" (they come at about the same price anyway).

  12. amanfromMars Silver badge
    Alien

    AIMi56IOn Accomplished, Einstein* ..... Wanna swap Colossal Tales and Shake ITs Booty**?

    Wow, after reading those comments, who could possibly ever claim that alien life isn't real with ITs IntelAIgents not up and bunning, carving out niche Vistae/ControlLed Parallels? .

    *.... http://www.theregister.co.uk/2008/04/09/chertoff_cyber_security/

    ** Astute SuperSubAtomic NEUKlearer ProgramMIng for AIReality System Virtually dDeliverable and dDelivered.

    Intelligent AIdD/PS: If you have to ask ....."How much?" ..... without first making a sensible offer, which won't be turned down and held against you, but rather virtually used to help Mutually, you aint qualified or cleared high enough to know and/or understand. Then would IT require a Crazy Offer to Help IT XXXXPlain Everything Planely...... and Succinctly.

    I Cisco Kid You Not.

  13. Sceptical Bastard
    Coat

    I bet those buns...

    ... use a lot of currant. And if they get too hot, they can be iced - otherwise they'll be toasted.

    Mine's the brown one dusted with cinnamon

  14. Anonymous Coward
    Coat

    But..

    What possible raisin could anyone have to run Vista on one of these?

  15. Valdis Filks

    Water cooling P6 adds extra costs and complexity.

    Water cooling for CPU's is an admission of a design failure. The extra pipework and electrical power to run the water cooling just adds costs and complexity. Extra electicity is required to run all the water cooling, so there are not savings, this needs to be taken into account and cannot be a hidden infrastructure cost. Plus to add an extra water infrastructure to a computer center with all that electrical wiring is dangerous. Computers and water do not mix well together. Using water cooling for computers is a technological backward step.

    All described here: http://blogs.sun.com/ValdisFilks/entry/water_and_electricity_do_not

  16. amanfromMars Silver badge
    Alien

    Einsteins Mate, Matey ...... Pandora's ProXXXXi Box Index*.

    Rather than getting drunk as a skunk at work on beer alone, in the best of BOFH/PFY traditions, here is a spirited chaser which obviously got knocked over and Lost in Space.

    And just like the bus which arrives whenever you really don't need another one, it is still always reassuring that such shit happens, all the Time, every time when you need one.

    Lest we forget ... A Prized Possession but Only when IT is Wwwidely Shared

    By amanfromMars

    Posted Wednesday 9th April 2008 05:45 GMT

    "And then the things you can do are limited only by your imagination. There is some seriously scary potential there." .... By Nexox Enigma Posted Wednesday 9th April 2008 03:31 GMT

    Control Imagination and no one will be scared off some Virtually Real Opportunities, with no Limits, Nexox Enigma.

    And there would be some seriously scary potential there..... with ControlLed Imagination. As you may like to Imagine, that would be "unusual" in present extremes and probably considered not normal/paranormal. However, in AI, IT is Normal Default and therefore the Status Quo Future Parameter/CyberIntelAIgent Protocol ....... and Worth a Mint .... which makes IT QuITe Valuable.

    Do you Think IT is Readily Available Today for Futures, the Derivatives of Tomorrow ... as AI ZerodDay Trading Commodity/Virtualising Asset/Creative Force?

    amfM HyperRadioProActive Network InterNetworking says Yes/Ja ........ and Registers IT so here, in the here and now.

    http://comments.theregister.co.uk/2008/04/09/dns_rebinding_attack/

    * And yes, that is Trading Relative to the Deutsche Boerse and Teutonic IT Engineering ....... FabKraftWerk

  17. stizzleswick
    Coat

    Re: Water cooling a bad idea

    That's probably why Seymour Cray's "design failures" were cooled by liquid nitrogen instead... (yes, I know that was because of the superconducting interconnects, not waste heat from the processors...).

    Anyway, Valdis, how about putting the gear in an oil bath? I have seen at least one attempt at that work pretty well so far (admittedly not on the same scale as the IBM systems).

    Mine's the one with the copper plumbing on the back.

  18. Jason Togneri
    Alert

    @ Valdis Filks

    In an enterprise situation, yes; you don't want water in your datacentre, period. But for the home user who prefers the extra quiet, there's absolutely nothing wrong with it!

  19. Anonymous Coward
    Anonymous Coward

    Water cooled.....

    You could also use it as a giant coffee machine.

    "Fire up the database Geoff, I need a double skinny latte" (whatever that is).

  20. Anonymous Coward
    Gates Horns

    Vista

    You're all missing the point with vista...

    The point is that microsoft will see this machine as a base spec for windows 7, and be able to say "Windows 7 will run adequately on machines as old as early 2008" (bearing in mind the release date will slip, early '08 will seem like ancient history) Note I said adequately, you'll need a cluster of these for reasonable performance (ie equivalent to Win 3.11 on a 486).

  21. Steven Jones

    Water Cooling

    Good heavens - water cooling in data centres is dangerous? Well we managed back in the 70s and 80s without too many people being electrocuted on mainframes back in the days of ECL chips. In fact it can make a great deal of sense to use liquid cooling as it is a far more efficient way of carrying high concentrations of heat than is using air (a tad quieter too - the air cooling systems oin some disk arrays can be so loud as to require the use of ear defenders). Note that virtually all car engines are liquid cooled, not air-cooled. Gas cooled nuclear reactors turned out to be a dead end and liquid cooling has won out.

    Using water cooling has one considerable advantage - it's possible to export the heat directly outside the building and not have to do through a process of cooling air, pumping the air through the building and then heating it up.

    Of course it's better not to generate the heat in the first place, but for some sorts of workloads which cannot be readily split or which depend on single-thread processing speed (read huge, high-thoughput database servers as the prime example) then there often isn't a lot of choice.

    I suspect that most IT people don't come across the sort of monster workloads that suit these beasts. There isn't a need for a vast number of them, but for certain applications they most certainly are needed.

  22. Dunstan Vavasour

    Water Cooling

    I disagree with Valdis.

    Air cooling is inefficient and results in significant power wastage. If the heat can be removed with water to some central point where it can be lost, there will be significant energy savings relative to running CRAC units to keep an arctic datacentre. Water cooling also enables the datacentre power density to be much higher, instead of the rule-of-thumb 4KW per rack which is as much as conventional raised floor cooling can handle without hot spots.

    The inhibitor on water cooling is that nobody wants to break ranks first. Kudos to IBM for going first on this. While I remain to be convinced whether cranking Power 6 up to 5GHz will offer any real customer benefits, it's entertaining to watch.

  23. The Mighty Spang
    Coat

    Re: VIsta

    I donut know what the problem is here...

    I choux-dn't worry too much about it though

  24. Arnold Lieberman

    Greener than given credit for?

    Surely with so much hot water being circulated, it could be "lost" to the building during winter, thus saving money on the heating bill...

  25. Anonymous Coward
    Alert

    @ Valdis Filks

    Totally wrong, how many 30watt fans do you need to cool the whole screaming rack? compared to one ity bitty water pump.. Additionally how many KW are you using on Aircon? because running a hose out of the building to an external radiator is way cheaper! Water cooling is far more efficient as one litre of water holds 2000 times more heat than 1 litre of air and its only 100 times heavier!! (or is that more massive?) hence the water runs at least 1000 times slower, and because it only needs to run slow a low pressure is needed say about 0.5m head. so just a tiny pump (20-50watt?) will keep the water flowing around the whole rack...

    The contrasting levels of noise should give you a clue about power efficiency.

  26. Anonymous Coward
    Thumb Up

    I could use one of these

    To give myself a fighting chance of beating my son at the ancient board game known as go. Problem is it would be my simulated annealing programming and this nice piece of kit that would beat him not me. Probably not for long at the rate at which he's improving - going from a 2 kyu to a 3 Dan player in about a year.

    Why I'd want to slow something like this down to z80 equivalent performance by running Vista on it is somewhat beyond me.

  27. Ru

    Re: Greener than given credit for?

    This could equally be done with an aircooled datacentre. Cambridge University's computer lab can have its waste air pushed through the building's heating system in winter, for example.

  28. Valdis Filks

    Water cooling

    A couple points, raised in these comments, which I will try to answer.

    1) Yes we used water last century in datacenters. But that is because we did not have a choice. When aircooled systems became available we had a choice and kicked the water cooled computers out very quickly, to be replaced with air cooled computers.

    2) Water cooling on occassion failed, leaked, had to be switched off, water cooled servers needed to be switched off. Things got really ugly, I worked in v.large datacenters I saw these problems. Someone mentions that we used water without too many people being electocuted, to me one such water cooling disaster is one too many. Avoidance is a better policy.

    3) Air cooled servers could coutinue to run, while water cooled servers needed to be switched off, when the safety guys decided the water leaks were too much of a risk in a high voltage datacenter then we had to switch off everything.

    4) Yes water may be a better coolant than air, it adds complexity though. Magnox is a better coolant (shorter half life) in Nuclear reactors than water in PWR. But magnox much more complex to maintain than water. In the same way that water is more complex to manage in a datacenter. Using oil is just another level of complexity.

    5) Are we proposing that we justify to buy a computer to help heat the building. When we decommission a water cooled server, do we need to buy extra boilers to heat the building. This is a plumbing nightmare, lets keep things simple. Again, water cooling adding complexity.

    We are back to the starting point, do not make hot chips that require water cooling. Maybe I am too risk averse. But I worked with big computers (mainframes), then Amdahl and Hitachi came along and made air cooled machines. Which sold like hot cakes as they did not require all the extra baggage of water pipes, cooling, power, monitoring, maintenance. If you want to scare the hell out of a datacenter manager, tell him he has a water leak in the datacenter.

    Prevention is better than cure, do not use water cooling.

    I am not that old, but strive for simpler computer architectures avoiding the mistakes of the past. Have we learnt nothing from our computer heritage.

  29. Stephen Booth

    Water cooling

    I'm with the pro water cooling crowd.

    Water cooling might be a bind if you are thinking in terms of a small server cupboard cooled by through the wall air-con units, but once you have a whole building full of the beasts then your air-con system has to be driven by a massive chilled water plant anyway.

    In this case getting the chilled water closer to the source of the heat has to reduce the overall power use.

    The only time I remember a big puddle of water under the machine room tiles it was not a failure of the chilled water system but the dehumidifier drain pipe got blocked and it was the air-con system that caused the flood.

  30. Fluffykins Silver badge

    Sooooooooooo

    We struggled with the Stone Age,

    Battered our way through the Bronze Age

    Ground through the Iron Age,

    Had a bit of fun with the Industrial Revolution

    Entered the Space Age

    Landed in the Garb Age

    And are now having a second go with a renaissance of the Steam Age

  31. Anonymous Coward
    Thumb Up

    Water Cooling = Warming Water.

    Hmmm, if they could plum the output into the central heating system somehow - more energy savings.

  32. Martin Maloney
    Dead Vulture

    Watt-er cooling?

    I guess that that's the reason for all of the hot cross puns!

  33. Robert Hill

    @Valdis Filks

    Hitachi and Amdahl pushed air-cooled solutions because they were competing with IBM on price, whereas IBM was compteting on having better performance. IBM knew that Emitter-Coupled Logic (ECL) was a faster clocking solution than CMOS or NMOS at the time, and that despite the heat they would have a performance advantage on the very heaviest workloads.

    Eventually, CMOS and NMOS gained in clock speeds, and even IBM made the transition - but acknowledged that the individual processors were slower than their predecessors. Today's energy-efficient CMOS processors require massive paralleization to compete with either more complex CMOS designs (i.e., the original scorching Pentium IV, et al) or ETL successors.

    And what has the parallization of processors brought? An acknowledgement that for many sorts of problems, we can't effectively write parallel code. That's why Intel and others are crash-researching parallel coding techniques. That is why IBM continues to push the speed of individual processors, even to the point of resucitating water-cooling in the data center.

    Now, that's not to say that MANY problems don't decompose well into parallel solutions: parallel databases have revolutionised data warehousing, clusters are wonders of mainstream application hosting, etc. But for several, important, and PROFITABLE types of workloads (esp. some scientific work and mathematical work, as well as some database solutions) individual processor performance are the limiting factor.

    Lastly, I would be curious to see how the water cooling on these corresponds to the watercooling in old mainframes. Are they running the pipes within the case to radiator fans (as in a watercooled PC), or running them external to the case via datacenter cooling lines as in the old mainframes? In short, what is the real level of complexity?

  34. Anonymous Coward
    Paris Hilton

    @Valdis Filks

    >> Water cooling for CPU's is an admission of a design failure.

    >> All described here http://blogs.sun.com/ValdisFilks/entry/water_and_electricity_do_not

    Sun engineer decides water cooling is a design failure same day as IBM kicks Suns butt.

    Could Paris smell the sour grapes?

  35. Valdis Filks

    Parallelism and water cooling.

    The water cooling is a risk assesment, reduce the components involved and simplicity always is a better option.

    For example you can have, in your infrastructure:

    Design A = Power (electricity), Network (electricity), SAN (optics mainly), cooling (air)

    Design B= Power (electricity), Network (electricity), SAN (optics) and cooling (air + water)

    Design B has more components plus a catastrophic mixture of water and electricity. This is the problem, even if you use it to heat your building, your infrastructure just got very complex and dangerous, by adding water. Your safety regulations and such like has just increased costs.

    Parallelism, this is also a virtualisation play.

    With a low power air cooled server which has 8 cores you can virtualise 8 single threaded apps. You use the free software and the system to create 8 domains. As some of these cores can have more than one thread e.g. 2. You could even consolidate 16 servers or to one of these highly multithreaded servers which are 2U in size and go by the name of coolthreads. No water cooling required.

    However, lets take any mainstrean already existing database e.g. MySQL, Oracle, Postgress and DB2.

    These have many parallel processes (often more than 8) e.g. db writer, lock manager, transaction manager and so on. So put these on a multi core/thread server and you have a good match. No coding/changes/migration required. A very large majority of servers are running OLTP workloads that have a database engine as described above so a very large segment of the computer/server market is ideal for parallel computing.

    Long term agree, need to write better parallel apps. But a lot of apps (OLTP) out there are parallel in nature already.

    Can't quite agree on the water cooling, but I am open to suggestions.

  36. Bronek Kozicki
    Coat

    Water cooling

    If we really did not want to have water in data centres, we wouldn't be able to use air conditioning there (ever heard of condensation?). Secondly, any fluid is more efficient in moving heat from one point to another than air - it really doesn't have to be water. Lastly, invention of wheel was technological backward step, too - we all should be able to carry around whatever we need by means of genetical engineering, of course.

    Mine is the wet one.

  37. Matt Bryant Silver badge
    Pirate

    RE: Valdis Filks

    Lol, do I spot a bit of the old company line there at blogs.sun.com? Sun doesn't have a chip now powerful enough to kick up any real heat so Valdis pops up to knock the competitor's kit. Bit rich considering that whenever I have to go to visit any hosted sites, if the room is cold I usually look for a rack of the old SPARC kit to stand behind whilst I do any paperwork, it's always much hotter than even modern blades!

    Watercooling is a great idea when you have very hot kit in small spaces. And with modern kit I have yet to see a single leak. Watercooled racks have been available for a while, and they do help with local cooling in those datacenter rooms that just don't have enough airconditioning. They also do reduce noise as they are usually closed racks, bit like your average family car with its modern watercooled engine is a darn sight less noisy than that old VW Bettle with its aircooled one.

  38. Anonymous Coward
    Anonymous Coward

    Flawed thinking

    Re: "Water cooling for CPU's is an admission of a design failure. The extra pipework and electrical power to run the water cooling just adds costs and complexity. Extra electicity is required to run all the water cooling, so there are not savings, this needs to be taken into account and cannot be a hidden infrastructure cost. Plus to add an extra water infrastructure to a computer center with all that electrical wiring is dangerous. Computers and water do not mix well together. Using water cooling for computers is a technological backward step."

    Totally flawed thinking. Your suggesting that it's not worthwhile using water cooling as it requires electricity which would negate the benefit caused by the cooling process itself.

    Total rubbish. The idea behind water cooling is to cool the hot processor, to allow that processor to run at a high clock frequency. Who cares if the cooling system requires some electricity to run it, the goal is not to save electricity, the goal is not to prevent the heat being generated, the goal is it to allow the processor to run at 5GHz to take that heat away from the chip and if water cooling is the way to do it then that's the way to do it, if forced air cooling is not sufficient.

    What do you suggest? Not use water cooling, if so, what do you then do? The chip will burn out and be completely useless.

    Think about automobiles, in most the engines are water cooled, and yes, it requires electricity to pump the water round.

    By your argument, nearly every automobile that has ever been made is a design failure which is clearly nonsense.

    Years ago, mainframe computers used ECL (silicon based chips) which drew considerable more current than current CMOS/MOS technologies, they were water cooled. If properly designed then it's not a problem.

  39. Ben
    Boffin

    Fluorinert

    I'm surprised nobody has mentioned Fluorinert - I once worked with some Cray machines that used the stuff. Conducts heat away better than air, and is electrically insulating so less of a problem if it leaks. I don't know of any modern machines that use it though? The trend seems to have been to use large quantities of standard processors rather than specialist chips, and so I imagine there is less need to use specialist cooling techniques.

  40. Valdis Filks

    Water cooling adds complexity.

    Agree, water is used in chillers in the datacenter, most of the computer rooms that I have been in, the air con units/chillers are in the periphery/edges of the rooms. What water cooling to servers/computers does is put pipes and plumbing all over/under the floor mixing it with the network, SAN and electrical power. Do we need an extra substance/piping under the floor. Does it create more problems than it solves. I have seen many companies go through projects to simplify and reduce their underfloor/overhead wiring. Some datacenters even have alarmed floor tiles. Why do you want to mix water pipes with this.

    The point of this is to reduce complexity, less is more, simplicity is better than complexity.

    All computer manufacturers should help give the computer industry a good reputation for technology leadership by reducing complexity. This is the point about water cooling, it does not make things simpler for customers. Water cooling makes computing more complex.

    Do you want to say to your customer, here is a new server and do you know a good plumber, on 24hr call out, 7 days a week.

    NB I do not write anonymous but am open and stand behind my beliefs. I was born in a country and live in a country where free speech is respected. Do anonymous writers/comments have something to hide ?

  41. SB

    Air cooling aint that great...

    back in the IBM water cooled mainframe days it was the AIR cooling devices that were failing, not the WATER cooling. Dead fans caused more outages than anything else. So now there's redundant fans all over the place...not exactly simple...or quiet...or efficient. How many blade racks have caused hot spots in computer rooms due to expelling too much hot air?

  42. Ed Cooper

    I can't help but think

    In these days of high energy costs, and growing environmental concerns, that water will win. You can dump heat from a water system by pumping it through a pipe in the ground. You could easily heat exchange it into an existing HW system. With a bit of forethought even the worst plumbing failures could be manageable - with reduced capacity.

  43. stizzleswick
    Stop

    Re: Fluorinert

    Fluorinert is a CFC, therefore has been banned from use in most countries in the 1990s. That's why modern machines don't use it. One could, however, have a look at the compounds used in modern refrigerators...

  44. Anonymous Coward
    Anonymous Coward

    More watercooling opinions

    The critique of watercooling as I see it has a main flaw. While much of the reasoning in the examples is ok and appropriate the generalisation does not follow. So while it may very well be the case that there are questionable implementations of watercooling this is not a natural result of the principle of using watercooling. As a complementary proposition it is perfectly feasable to imagine flawed aircooling solutions. As I have come across quite a few I do not even have to use much imagination for this. And it is true that we could find many flawed watercooling systems that also fail. It is also true that we could find systems where watercooling was put as an afterthought because the original objectives of the design were not met. However this does not mean that it could not be possible to design intentionally a solution with watercooling (e.g. not a result of a 'design flaw'). In any specific practical implementation such a solution does not by default have to be more prone to failure than a specific aircooling solution. Compare to a car engine, while it could be argued that watercooled car engines in general add complexity (and would in principle than be more suspectible to problems) this does not necessarily mean that air cooled engines are more reliable in practice. We should also remember that if complexity is something we do not like than maybe we should stay away from all things IT - what about the result of moores law?...

  45. John Savard

    One thread, one processor

    Overclocked gaming PCs use water cooling, but not in the same fashion as the mainframes of old. So I think that the risk of leaks can be avoided. Since the real need for high speeds is for problems that are serial, I would think that a limited number of hot, high-speed chips would be needed, and the parallelizable part could be taken care of by slower multi-core chips that produce more throughput per watt. It would be nice to get a desktop machine with just one of these high-speed processors, but it would have to run Linux, not Vista, not being x86.

  46. Anonymous Coward
    Thumb Up

    Fwoarrrrrrrrr

    I could really tarfu the weather forecasts with one of those.

  47. Matt Bryant Silver badge
    Happy

    RE: Valdis Filks

    "...The point of this is to reduce complexity, less is more, simplicity is better than complexity...." Erm... yeah, right, can we now expect the next Sun APL server to be a badged abacus then (as opposed to badged FSC)?

    I know! All that SAN stuff is just sooooo complex, lets just go back to locally-attached SCSI disk for all servers and forget the savings on utilisation and administration, and we'll get rid of all those pesky fibre-channel cables from under Valdis's floor tiles as well! And who needs file-servers, lets just give all our users USB keys and tell them to transfer files between systems that way, we can then cut back on gigabit cabling and free up even more under floor space! And people wonder how StorageTek ever got to the point where Sun bought it....

  48. Anonymous Coward
    Flame

    @ RU

    Actually the entire computer science building is passively cooled and heated. Hence why the place gets so damn hot in the summer and why they always want all the computers in the labs on during the winter...

  49. Brian Miller

    RE: Valdis, water vs air cooling

    If the machine did not use water cooling, then it would use heat pipes with gargantuan fins to disipate the heat into the air. The fins for just one CPU would be enormous. The fins for *32* CPUs would mean that the case would either have to be huge, or else take another rack space behind it for the CPU fins.

    I have worked in datacenters where I had to wear ear muffs so I wouldn't be deafened by the fan noise. The datacenter at Microsoft which has two HP Superdome servers has cold air running through it like a wind tunnel. Nobody stayed in that room longer than they absolutely had to.

    Now consider water cooling. Water is inexpensive, and easy to handle. Large HF transmitters are water cooled, with the tubes in direct contact with pure circulating water, and nobody gets electrocuted and the equipment runs fine. Fluorinert is horribly expensive, and water is, well, cheap as water. Yes, plumbing is a problem if your plumbers are incompetent.

    From what it looks like, your position is that anything other than air cooling is a failure. Sorry, 'tain't so.

  50. Martin Usher

    Liquid cooling?

    Makes sense for situations where you've got to conduct a lot of heat away. You trade off the extra infrastructure for efficiency, quietness, even heat distribution (important) and even the potential to recycle some of that energy. Most car -- and motorcycle -- engines are liquid cooled (it may be a surprise to know that many bikes are liquid cooled, the fins on the engine are just for show).

    Air cooling in data centers doesn't make sense. You make a lot of noise (and spend a lot of energy) transferring the heat to the air only to have to remove it using liquid cooling through air-conditioning. Its much better to cut out the middleman.

    Water works well. I've been on a project where we used de-ionized water because we had to plumb it to a tube anode running at 7.5Kv -- taking the ions out renders the water non-conductive. For data center use, though, the water's more likely to be like the stuff in your car engine.